Hi all,
I've pretty much got my garage in a position where I can work in it, just need to get an electric supply in there!
I have spoken to an electrician and he reckons he can just take a feed from a new MCB in the house CU in t+e to a metal box in the meter cupboard and
run 3 core armoured cable straight out to the garage and terminate it at the metal CU in there. He discounted the fact we had a PME supply as the
garage is less than 5m from the garage.
Now have been reading up on this and it looks like there are lots of opinions on it. Some say exporting the earth from a PME supply is a no no and I
need to fit an earth rod and run a 10mm2 earth from that into the garage and then other say as long as the garage has no incoming metal parts such as
water pipes etc it is ok.
The garage is detached and about 2.5m from the house. it has no water pipes etc and is brick with a concrete floor. has anybody been in a similar
situation and what was done to get a supply to the garage?
Thanks,
Shaun
Not sure what the rules are on this - I've the benefit of a garage integral to the house with the house consumer unit in the garage. I used a
spare position in the consumer unit and ran a ring in the garage with plenty of sockets on it (more than I'd use at any one time). The wiring
was then changed again by a sparky to feed mains to an added conservatory via armoured cable. The wiring (including the garage ring) and consumer
unit was then tested and passed by the sparky.
I'd suggest getting advice and quotes from say 3 sparkys to see what each recommends to you.
Thanks for the info but that's not what I was asking!
P.S Why do the vast majority of your posts start with "not sure" or I "don't know but"? Not having a pop but seems like you
are just trying to get your post count up!
I have asked this on other more specialist forums but I know there are a few electrical peeps on here so would like to heard what they have to say!
Shaun
my garage is 10 meters from the house with pme . garage is fed with 3 core armoured with no earth spike , garage unit is plastic with the earths attached.
Thanks for the reply!
At least I know the sky won't fall in on me! I don't suppose you know if the armor is used as an earth as well as do you? And if so is it
connected at just the house end or both?
Thanks a lot,
Shaun
It is good practice to earth the armour at each end - there is a ring supplied with the
gland kits. I was advised to use 10mm earth wire terminated
incrimp lugs . It is connected to the earth bar within the CU.
Given the short distance from house to garage there shouldn't be any disparity between the earths but , as always, it should be signed off by a
proper sparky
The armour should NOT be used as the earth if a 3-core cable is being used, BUT the armour should BE earthed !
Personally, I would connect both ends of the armour to the earth terminals in the consumer units at each end.
Sorry - I should have said that the armour is earthed in addition to the earth cable of the twin & earth
Thanks for all the info, I think i'm going to run 10mm2 swa under the patio for him!
Thanks,
Shaun
Best practice is to use 3 core swa but separate the earth of house from garage earth. Easily done using insulated box for termination in the garage meaning the armoured is earthed from house supply. Then use an earth stake for garage earth and you MUST use rcd protection on the garage circuits. Just be aware if you sell your house the buyers will require certification for any Part P scam certifiable work, which this is.
Hi,
No problem with Part P, they guy who is more than likely be doing it is full ticket. I was just confused as there are so many different opinions on
it. The are are no extraneous metal objects/pipes etc in the garage so most of the literature says as long as the CPC (which would in this case be one
of the cores) is equal to the bonding in the house (10mm2) then all is ok - its just the supplier that might have a problem!
P.S Why do the vast majority of your posts start with "not sure" or I "don't know but"? Not having a pop but seems like you are just trying to get your post count up!
Shaun
I hadn't realised I started my replies in that way or that it may be an issue.
Not an issue with me
Cheers!
Cheers!
No ass kissing please it was just a question!
It makes no difference how they do it. A very minor technicality. I believe you're meant to use the house earth to protect the cable and a rod to protect the garage circuits, but in reality rods are shite, so either don't bother, or link them allttogether. It really makes no difference.