In the kitchen department.......
What gauge cable should I use to make a 4 meter extension cord for a domestic 3400 watt appliance?
Fred W B
HTH!
Based on 230V, your current is over 14 Amps.
Even if you buy a suitable sized flex (probably 2.5mm) the max fuse size is 13A so you will be replacing the fuse alot!
Its a mini oven, so that rating would only be with both plates and the oven going flat out, which won't happen in practice
Here we use 20 amp circuit breakers on plug circuits
Fred W B
[Edited on 2/6/10 by Fred W B]
Most large domestic appliences should be hard wired into the wall on a suitable isolater... these are normally fed directly from the distribution
board on 30A cables...
4mm squared would give you 32A
I'm not a sparky but I am doing a lot of this sort of stuff at the moment. I'd run 2.5mm˛ direct from the fuse box on its own 20A circuit
breaker.
HTH
Mike
South Africa has no fuses in the plug tops and they are round pin 15A. None of the pansy power plugs that we have here.
Only one big difference here in the UK the power stays on almost 99.999999% percent of the time
out there its the ESKOM lottery.
appliances over 2.5kw are normally hard-wired via a 20A DP switch usually back to a dedicated MCB (breaker) at the board. 2.5mm sq cable will run it but not via a plugtop as it WILL overheat and (hopefully) blow the plugtop fuse. Beaing in mind that the plugtop and socket are only designed to carry 13A also.
Thanks for the responses all.
Originally posted by MikeCapon
I'm not a sparky but I am doing a lot of this sort of stuff at the moment. I'd run 2.5mm˛ direct from the fuse box on its own 20A circuit breaker.
HTH
Mike
Perhaps you shouldn't be.
HTH
Mike
[Edited on 2/6/10 by Confused but excited.]
^^ you would be fine unless it was a long run, or subject to a derating factor. 2.5mm t&e cable surface clipped is rated at 27A over a specified distance.