Wiring advice for a lot of fluorescent tube fittings!
NS Dev - 17/9/10 at 06:41 PM

Any electricians shed any light (pardon the daft pun) on this one?

I need to wire up 28 x 58 watt 5ft fluorescent tubes (our new paint booth). They are twin fittings, i.e. 14 of them.

What cable should I use and what switch/switches and breakers.

Now before a bright spark says multiply 58 x 28...........I know that! I mean I assume I have to allow for startup current, they are switch start units not electronic start.

My "gut feel" is that 1mm cable, through two switches, and to a single 16amp mcb, would do the trick.................

Don't want to do it all and then it fail the wiring check when I have to get that done though!

Lastly, is it still legal under part P to use old colours cable? I thought it was but just wanted to check as I have a full roll of old colours 4 core 2.5mm swa that needs using up! (PS obviously I am referring to 3 phase colours here, though I guess the same rules apply anyway)

[Edited on 17/9/10 by NS Dev]


Peteff - 17/9/10 at 07:04 PM

They sell 1.5 t&e usually for lighting. Have you got the light fittings suited to hazardous locations ?


jacko - 17/9/10 at 07:04 PM

I hope they are the proper lighting for a paint booth [ sparks and paint spray/fumes don't mix ]


daniel mason - 17/9/10 at 07:07 PM

you cant run 1.0mm twin on a 16 amp mcb mate!


SteveWalker - 17/9/10 at 07:09 PM

quote:
Originally posted by jacko
I hope they are the proper lighting for a paint booth [ sparks and paint spray/fumes don't mix ]


I don't know anything about spray booths, but I do know about petrochem plants and if the lights for spray booths are anything like the ones for hazardous areas in petrochem plants, he'll also be needing the right cable and certified glands.


Stott - 17/9/10 at 07:29 PM

You can use 1.5 swa or 2.5 if you like though the 1.5 is fine current wise.

You don't really want to be glanding that off, in and out of every fitting though, what a potch. If it's doesn't warrant SWA, don't use it.

Don't use t&e either, that's a bad job really, it's for houses. One of the neatest and easiest ways is flex and stuffing glands, it'll be wired really quickly, much easier to terminate and the glands don't allow for dust ingress should that be important to you.

You can still wire in old colours I guess, assuming you fit the std "this installation contains wiring colours to 2 different versions of BS7671" sticker, but you'd have to check, but running 2.5 SWA for the sake of it as it's free - no ta!

Stick it on a 10A C breaker (1.5mm flex) and you'll be fine for those lights I'd have thought and the cable is safe.

ATB
Stott

PS, then again, what do I know, take my advice with a pinch of salt.

[Edited on 17/9/10 by Stott]


NS Dev - 17/9/10 at 09:35 PM

quote:
Originally posted by daniel mason
you cant run 1.0mm twin on a 16 amp mcb mate!


good point, don't quite know how I came up with that one!! Was thinking of two runs then forgot about that once i started thinking of the total current rather than the cable!!!

doh!


NS Dev - 17/9/10 at 09:37 PM

quote:
Originally posted by Stott
You can use 1.5 swa or 2.5 if you like though the 1.5 is fine current wise.

You don't really want to be glanding that off, in and out of every fitting though, what a potch. If it's doesn't warrant SWA, don't use it.

Don't use t&e either, that's a bad job really, it's for houses. One of the neatest and easiest ways is flex and stuffing glands, it'll be wired really quickly, much easier to terminate and the glands don't allow for dust ingress should that be important to you.

You can still wire in old colours I guess, assuming you fit the std "this installation contains wiring colours to 2 different versions of BS7671" sticker, but you'd have to check, but running 2.5 SWA for the sake of it as it's free - no ta!

Stick it on a 10A C breaker (1.5mm flex) and you'll be fine for those lights I'd have thought and the cable is safe.

ATB
Stott

PS, then again, what do I know, take my advice with a pinch of salt.

[Edited on 17/9/10 by Stott]


cheers, that sounds like sensible approach.

Yep was planning on using flex and stuffing glands, that's how we've done it on the existing booth

edit ps wasn't running the swa for the lights lol that was for another part of the job, the extract/intake blower motor feeds

[Edited on 17/9/10 by NS Dev]


NS Dev - 17/9/10 at 09:56 PM

quote:
Originally posted by jacko
I hope they are the proper lighting for a paint booth [ sparks and paint spray/fumes don't mix ]


nope, they are just weatherproof ones.

The extract rate is so high that there are never any paint fumes in the booth!! The flow rate will be around 15,000 cfm

The extract plant came from a truck paint building. Interestingly the building was fitted with explosionproof sealed lighting......so imagine my shock to find that the intake air, fed directly into the building, was direct gas flame heated!!! All original Junair installation!

Don't see much point in sparkproof lights when you can put an open flame in the air recirc with paint fume recirculating past!!

As the last safety measure, we use a magnetically sealed heavy reinforced pvc "tarpaulin" door which would just flap open if any overpressure built in there.


slingshot2000 - 17/9/10 at 10:11 PM

Lighting cicuits should be protected by a 6AMP mcb, not a 10AMP !
Old colours are not allowed normally, but ask the question of whoever is to do the inspection?certification, would hate you to wire up swa, only to be told it cannot be certified!


NS Dev - 17/9/10 at 10:23 PM

quote:
Originally posted by slingshot2000
Lighting cicuits should be protected by a 6AMP mcb, not a 10AMP !
Old colours are not allowed normally, but ask the question of whoever is to do the inspection?certification, would hate you to wire up swa, only to be told it cannot be certified!


re. the 6 amp mcb, that's what I thought, but if the total load on the circuit is more than 6 amps (which is is by some margin! ) then??

Yea will check on tbhe swa with my sparky


Telboy - 17/9/10 at 10:40 PM

A 10amp mcb is fine with 1.5mm t&e or flex. All new circuits should be covered by a 30 mA rcd to achieve the correct disconnection times , unless your cable is mechanically protected. Your not allowed to use the old coloured cable , sticker or no sticker it's a good few years old already even before you've installed it , any good sparky would not put his name on a test sheet with that on it. Go to edmonsons or newye and eyre it's only about £2 per mtr


nitram38 - 18/9/10 at 01:04 AM

Sorry to butt in, but surface run cables are excluded from RCD protection. Only buried cables should have them unless earth sheilded or deeper than 50mm.
You can still fit one for extra shock protection but its not a requirement. Disconnection times are improved by better earth loop impedance. So generally using larger cables. RCD's are used if you cannot get the earth impedance down low enough to operate a regular fuse, but its bad practice in a normal installations i.e one not using an earth electrode.
The required max impedance figures for each fuse type/size are in the regs book.
Your fuse/cable size will depend on the method of installation and enviromental temps as well as required current. There are factors in the regs to apply to the cable.
As for cable colours, as long as the new colours are used at the termination in the form of sleeving, you can use any colour you like for the cable.
Sorry, just done my 2391 testing and inspection and this stuff is fresh in me brain!

[Edited on 18/9/2010 by nitram38]


daniel mason - 18/9/10 at 08:41 AM

why not run 2 seperate circuits? on 2 x 6 amp mcb's
just a main from the fuse board to one switch, controlling half the lights
and another main from fuse board to a second switch controlling the other half!
also if the lights will be hanging from chains i would fit some sort of plug and socket arrangement at each fitting to enable them to be taken down easily!


rusty nuts - 18/9/10 at 08:52 AM

Just a thought , I had to get my old workshop rewired by a qualified electrician to keep my insurance company happy , It may be yours will expect the same?


NS Dev - 18/9/10 at 09:42 AM

quote:
Originally posted by nitram38
Sorry to butt in, but surface run cables are excluded from RCD protection. Only buried cables should have them unless earth sheilded or deeper than 50mm.
You can still fit one for extra shock protection but its not a requirement. Disconnection times are improved by better earth loop impedance. So generally using larger cables. RCD's are used if you cannot get the earth impedance down low enough to operate a regular fuse, but its bad practice in a normal installations i.e one not using an earth electrode.
The required max impedance figures for each fuse type/size are in the regs book.
Your fuse/cable size will depend on the method of installation and enviromental temps as well as required current. There are factors in the regs to apply to the cable.
As for cable colours, as long as the new colours are used at the termination in the form of sleeving, you can use any colour you like for the cable.
Sorry, just done my 2391 testing and inspection and this stuff is fresh in me brain!

[Edited on 18/9/2010 by nitram38]


cheers, that's all nice to hear!

The lights in the booth will actually be on an RCD anyway, though that's more by co-incidence as I will be feeding them from the consumer unit that I'm putting in the office on the mezzanine above, which will be RCD protected as it will have some sockets off it.

I did think that surely the wiring colours must be ok if marked/covered appropriately at terminations (its what we did at my old work when I was last doing 3 phase installations there a couple of years ago)

Re. the earth loop impedance, I did run into issues there with my initial installation, but not in a way that you would come across in a domestic type installation! I had to use a D type breaker for my hydrovane compressor, as when the star-delta timer changed over it tripped a C-type out 2 times in every 4 starts. Problem was the D-type needs a ridiculously low earth impedance (can't remember the number) and the main feed into the building just would not get it low enough. I guess some earth spikes might be required?? In the end I had to up the feed cable size and go to a bigger C type breaker to achieve the same result without the earth issue!

Anyway, this swa is not that old, and will be fine, and £2 a metre might not sound much but it bloody adds up on long multiple runs (need 100m approx! )


NS Dev - 18/9/10 at 09:46 AM

quote:
Originally posted by rusty nuts
Just a thought , I had to get my old workshop rewired by a qualified electrician to keep my insurance company happy , It may be yours will expect the same?


All the wiring in the workshop is pretty much brand new. I installed most of it last May, and the stuff I am talking about now is all new installation. I only mentioned the swa in old colours as I have 100m drum that is not that old but needs using up.

Re. needing a rewire, it would only "need" a rewire if the existing installation could not be made to pass certification. If earth impedances cannot be got low enough, and earth faults exist, then with very old wiring its often quicker to just start again, but everything in my workshop is basically new.

The reason I do it myself, and using s/h stuff if I can, is to keep costs down as we don't borrow ANY money in our business. I am building a mezzanine floor, new upstairs office and a huge floor extract paint booth, all on a very low budget (under £4k for the lot)


NS Dev - 18/9/10 at 09:48 AM

quote:
Originally posted by daniel mason
why not run 2 seperate circuits? on 2 x 6 amp mcb's
just a main from the fuse board to one switch, controlling half the lights
and another main from fuse board to a second switch controlling the other half!
also if the lights will be hanging from chains i would fit some sort of plug and socket arrangement at each fitting to enable them to be taken down easily!


cheers, will prob do it like that, and have each side bank on seperate circuit. I was just puzzled by somebody's statement that lighting MUST be on a 6a mcb, when surely it must be on whatever mcb is appropriate to the cable used!!


Liam - 18/9/10 at 11:01 AM

I think Rusty's point was not about the necessity of a rewire, but that his insurance company required electrical work to be done by a qualified spark. Worth thinking about. I'm not really up to speed on commercial installations/insurance matters though. Are you expecting to get a spark in afterwards to test, inspect and issue all the paperwork?

The reason most lighting circuits (at least domestic) dont exceed 6A is the roses and or switches may only be rated at 6A - it's not just the MCB and cable on a circuit, ya know . Most domestic switches are rated 10A nowadays, but it's still uncommon to see circuits over 6A. Commercial is a different matter, but check the ratings of fittings etc if you're going over 6A. Personally I'd make this lot at least two, possibly more 6A circuits on at least C-type MCBs ELI permitting.

Using old colours would have to be listed as a departure from the regs on the EIC/MWC. You need a good reason for making the departure and it must not reduce safety. For example an acceptable reason for using old colours could be that the existing installation uses old colours and so sticking to old colours reduces the possibility for confusion and therefore increases safety. Because you have some kicking about wouldn't wash imho, especially if the rest of the installation is new colours. Sleeving all the old colour cable with new colours at the terminations might make it acceptable - would be up to the inspecting spark (if that's you fine!).


rusty nuts - 18/9/10 at 11:10 AM

Thanks Liam , That's exactly what I was trying to put over.


Liam - 18/9/10 at 01:11 PM

In fact, thinking about it, and bearing in mind I'm a sad geek, I'd definately have it on three circuits. One with 4 lights, one with 8 lights, and one with 16 lights. Then you can have binary dimming with combinations of the three switches as per this logic table...

S1 S2 S3 Lights
0 0 0 0
1 0 0 4
0 1 0 8
1 1 0 12
0 0 1 16
1 0 1 20
0 1 1 24
1 1 1 28

How totally awesome is that?





I'll get me coat

[Edited on 18/9/10 by Liam]


Stott - 18/9/10 at 03:33 PM

quote:
Originally posted by slingshot2000
Lighting cicuits should be protected by a 6AMP mcb, not a 10AMP !




You fuse to protect the cable irrespective of load, cable is specced for the load.

Total load of this circuit is nearly 7 amps not allowing for inrush current, so a 10A C type would protect the cable and allow for a delay in the trip characteristic on startup.

If you've got 1.0mm t&e buried in the walls or insulation in lofts in a house, and it's only running 5 fittings at 100w a pop, then after corrections, you'd end up on a 6A as this is correct to protect the cable.

There are at least 3 methods in the 17th Ed that allow for a 10A mcb on 1.0T&E.

It's all dependant on the installation.

ATB
Stott


NS Dev - 20/9/10 at 08:48 AM

quote:
Originally posted by Liam
I think Rusty's point was not about the necessity of a rewire, but that his insurance company required electrical work to be done by a qualified spark. Worth thinking about. I'm not really up to speed on commercial installations/insurance matters though. Are you expecting to get a spark in afterwards to test, inspect and issue all the paperwork?

The reason most lighting circuits (at least domestic) dont exceed 6A is the roses and or switches may only be rated at 6A - it's not just the MCB and cable on a circuit, ya know . Most domestic switches are rated 10A nowadays, but it's still uncommon to see circuits over 6A. Commercial is a different matter, but check the ratings of fittings etc if you're going over 6A. Personally I'd make this lot at least two, possibly more 6A circuits on at least C-type MCBs ELI permitting.

Using old colours would have to be listed as a departure from the regs on the EIC/MWC. You need a good reason for making the departure and it must not reduce safety. For example an acceptable reason for using old colours could be that the existing installation uses old colours and so sticking to old colours reduces the possibility for confusion and therefore increases safety. Because you have some kicking about wouldn't wash imho, especially if the rest of the installation is new colours. Sleeving all the old colour cable with new colours at the terminations might make it acceptable - would be up to the inspecting spark (if that's you fine!).


Yea will all be checked by sparky once done, yep my insurance demand the same. I just don't like paying a sparky more per hour than my own labour when I can do the donkey work myself.

The only "problem" with my last installation (the whole of my unit, incl 2 x 3phase dis boards etc etc) was the ELI issue with my D type breaker on the compressor.

ps weighing in the old cable and buying new, scrap man offered enough for it to make the descision!


omega 24 v6 - 20/9/10 at 03:20 PM

I may stand to be corrected BUT IIRC the start current multiplyer for fluorescent tube was 1.8 ( Form memory)
So 28 x 58 x 1.8 =2923 watts/240 volts
Is 12.2 amps approx. so your cable and switchgear will need to be able to handle 16 amps ( or nearest sized mcb)


Stott - 21/9/10 at 03:59 PM

^ yeah I think that's right, 12.2 at startup, 7ish running, so 10A C type and 1.5 flex will cope just fine.

The flex is rated at about 16A depending on manufacturer and the trip charectaristic of a C type curve breaker should allow for the startup current without tripping

ATB
Stott
Stott


JoelP - 21/9/10 at 05:35 PM

if it did trip the breaker, you could always up it to 16A and back down to 13A via a fuse.