Author: Subject: Freezing weather and CH pressure
tegwin

posted on 29/11/10 at 09:58 PM Reply With Quote
Freezing weather and CH pressure

A slightly odd and disjointed question, but cant quite get my head around it..

Normal pressurized central heating system (with expansion vessel) set to 2bar....

If parts of the system freeze what pressure would the pressure vesel guage show?





Reason I ask.... my grandmothers heater is complaining that there is now flow through it (or low pressure).... the pressure guage reads as 0-bar... the temp has been below freezing for some time so its possible some of the pipework has/is frozen...

Trying to work out if the pressure will come back when it thaws, or if the pressure loss is likeley to be caused by a broken pipe somewhere...





------------------------------------------------------------------------------------------------------------------------
Would the last person who leaves the country please switch off the lights and close the door!

www.verticalhorizonsmedia.tv

View User's Profile Visit User's Homepage View All Posts By User U2U Member
cliftyhanger

posted on 29/11/10 at 10:05 PM Reply With Quote
hmm, if frozen bits that will not reduce the pressure. Of course a leak will.....
Have you topped up the system and tried again. Some need topping up from time to time (but not often, my home one about 2-3years, another rented house about 8 months) so it may have been losing pressure for some time? It will soon show where the leak is too
Best to avoid leaving these things without frostguard settings, just too much could go horribly wrong.....

View User's Profile View All Posts By User U2U Member
mookaloid

posted on 29/11/10 at 10:05 PM Reply With Quote
Usually pressure drop is caused by a small leak in the system - so unlikely to come back if the ambient temp goes up again





"That thing you're thinking - it wont be that."


View User's Profile E-Mail User View All Posts By User U2U Member
adam1985

posted on 29/11/10 at 10:06 PM Reply With Quote
i would of thought the pressure would increase when water freezes it expands this is why it splits pipes (not enough to notice on the guage though) the low pressure is more than likely a little leak somewhere check the pressure relief pipe outside isnt dripping too

[Edited on 29/11/10 by adam1985]

View User's Profile View All Posts By User U2U Member
paulf

posted on 29/11/10 at 11:15 PM Reply With Quote
If it is the type of pressure vessel with a bladder in it to hold the air then it is possible that the air has escaped and then a small change in the volume of water in the system due to temp etc will cause the pressure to drop to zero.
Paul

View User's Profile View All Posts By User U2U Member
NigeEss

posted on 29/11/10 at 11:49 PM Reply With Quote
Had exactly this problem today, pressure dropped to zero, boiler (condenser type) shut down and displayed a fault
code.

Turned out to be the outlet pipe from the condenser had frozen outside the wall and blocked. Thawed it out and
re-pressurized the system and all is well. No Idea why the pressure dropped though. Had it been an auto dump
I'd have expected to see water somewhere but no.





Time is an illusion. Lunchtime doubly so.................Douglas Adams.

View User's Profile View All Posts By User U2U Member
tegwin

posted on 30/11/10 at 12:30 PM Reply With Quote
Hmm.. have suggested she re-pressurises the system and sees what happens...
View User's Profile Visit User's Homepage View All Posts By User U2U Member

New Topic New Poll New Reply


go to top






Website design and SEO by Studio Montage

All content © 2001-16 LocostBuilders. Reproduction prohibited
Opinions expressed in public posts are those of the author and do not necessarily represent
the views of other users or any member of the LocostBuilders team.
Running XMB 1.8 Partagium [© 2002 XMB Group] on Apache under CentOS Linux
Founded, built and operated by ChrisW.