garden wiring question- additional daft questions!!

Guys,
we're wiring some lights etc in a garden.
There is a main feed to a control panel, which has a control system
this feed is a wire armoured cable...

my question is -

i'm assuming that i can run wire armoured cable with no trunking. i.e. striaght in the ground.

Assuming the standard Type P 500mm buried and marked with marker tape, is this ok?

And i know that my local building control officer needs to inspect etc ;-)

[Edited on 2/5/06 by Jumpy Guy]

View User's Profile View All Posts By User U2U Member
jono_misfit

posted on 28/4/06 at 02:12 PM Reply With Quote
Make sure you use a propper IP rated gland when terminating the armoured cable. Sounds daft, but lots of people seem to use indoor gland then wonder why they've got shorts.

Been ages since ive worked with a trenched cable, but think you need to use a bed of sand under the cable.

View User's Profile View All Posts By User U2U Member
rusty

posted on 28/4/06 at 03:56 PM Reply With Quote
Think trench depth ay be 600 now.
View User's Profile View All Posts By User U2U Member
nitram38

posted on 28/4/06 at 05:35 PM Reply With Quote
Also ensure the circuit is protected by an RCD. Residual Current Device. With a 30mA trip. This is a requirement for all external wiring or out buildings. It will protect you from electric shocks.

Martin (IEE 16th Edition Electrician 236 Pt III)






View User's Profile View All Posts By User U2U Member
Jumpy Guy

posted on 28/4/06 at 06:16 PM Reply With Quote
thanks guys..

the 600 depth is only for allotments etc..

View User's Profile View All Posts By User U2U Member
Confused but excited.

posted on 28/4/06 at 06:21 PM Reply With Quote
Should also be covered with concrete copings with the elect. hazard warnings cast in on the top and the yellow warning tape layed above that.
ie:
sand bed
suitably rated armoured cable
copings
hazard tape
500mm of soil etc.( not including turf )
and of course all conection methods suitably rated for their location as previously stated.

That's a proper job, that is.

[Edited on 28/4/06 by Confused but excited.]





Tell them about the bent treacle edges!

View User's Profile View All Posts By User U2U Member
nitram38

posted on 28/4/06 at 06:25 PM Reply With Quote
As long as it is at least 500mm deep and has an rcd plus electrical marking tape, you will be ok.






View User's Profile View All Posts By User U2U Member
Browser

posted on 29/4/06 at 07:04 AM Reply With Quote
Or just do what Alan Titchmarsh used to do on Ground Force, run some standard flex through a length of garden hose






View User's Profile View All Posts By User U2U Member
nitram38

posted on 29/4/06 at 07:12 AM Reply With Quote
quote:
Originally posted by Browser
Or just do what Alan Titchmarsh used to do on Ground Force, run some standard flex through a length of garden hose


RCD protected though!






View User's Profile View All Posts By User U2U Member
Confused but excited.

posted on 29/4/06 at 02:37 PM Reply With Quote
quote:
Originally posted by nitram38
quote:
Originally posted by Browser
Or just do what Alan Titchmarsh used to do on Ground Force, run some standard flex through a length of garden hose


RCD protected though!


This is not good advice.
You should only use suitably rated flex for low voltage lighting ie; 12 - 24 volts.

[Edited on 29/4/06 by Confused but excited.]





Tell them about the bent treacle edges!

View User's Profile View All Posts By User U2U Member
JoelP

posted on 29/4/06 at 02:51 PM Reply With Quote
the rcd makes it less bad but armoured cable is always going to be safer.
View User's Profile View All Posts By User U2U Member
Jumpy Guy

posted on 29/4/06 at 05:47 PM Reply With Quote
Plan is-

230 V AC main feed to panel- 2.5 armoured, 500 mm down, haz. tape, laid on pea shingle, then sand.

24 V DC supplies to lamps - 1.5 armoured, as above.

RCD to each 230/24 transformer

only question left - part of the 2.5 armoured is directly embedded into concrete. - i dont have to run conduits or transfers, do i?

View User's Profile View All Posts By User U2U Member
nitram38

posted on 29/4/06 at 07:21 PM Reply With Quote
quote:
Originally posted by Jumpy Guy
Plan is-

230 V AC main feed to panel- 2.5 armoured, 500 mm down, haz. tape, laid on pea shingle, then sand.

24 V DC supplies to lamps - 1.5 armoured, as above.

RCD to each 230/24 transformer

only question left - part of the 2.5 armoured is directly embedded into concrete. - i dont have to run conduits or transfers, do i?


Yes!






View User's Profile View All Posts By User U2U Member
Lawnmower

posted on 30/4/06 at 09:48 PM Reply With Quote
or run it above ground in a conduit atached to your fence wall etc.
View User's Profile View All Posts By User U2U Member
Jumpy Guy

posted on 1/5/06 at 06:03 PM Reply With Quote
last question-

if i run armoured cable, propely clipped and saddled, along a wall, does it have to be in conduit?
if so, is plastic trunking ok, since the cable is armoured?

View User's Profile View All Posts By User U2U Member
nitram38

posted on 1/5/06 at 07:02 PM Reply With Quote
quote:
Originally posted by Jumpy Guy
last question-

if i run armoured cable, propely clipped and saddled, along a wall, does it have to be in conduit?
if so, is plastic trunking ok, since the cable is armoured?


No it can be clipped along a surface without any protection. You may want to protect it if it is likely to be banged alot.






View User's Profile View All Posts By User U2U Member
JoelP

posted on 1/5/06 at 08:41 PM Reply With Quote
remember uv light will degrade pvc sleeving over time, make it brittle and prone to cracking. A cheap plastic trunking will protect it.
View User's Profile View All Posts By User U2U Member
nitram38

posted on 1/5/06 at 11:08 PM Reply With Quote
quote:
Originally posted by JoelP
remember uv light will degrade pvc sleeving over time, make it brittle and prone to cracking. A cheap plastic trunking will protect it.


SWA cable is made to resist this. PVC twin and earth etc is not.






View User's Profile View All Posts By User U2U Member
Jumpy Guy

posted on 2/5/06 at 02:00 PM Reply With Quote
another 'Last' query-

I have 230/12 V transformers buried to supply some lights in the garden..

the cable from the transformer to the light fitting is 2 core water resistant cable..

I'm hoping that this doesnt need any form of protection or depth.... only 12 V DC

from what i can see, the legislation only covers the mains side, once its come up from the 500 mm deep transformer, the 12v side can be run along the surface to the lamps?

View User's Profile View All Posts By User U2U Member
Browser

posted on 2/5/06 at 02:43 PM Reply With Quote
quote:
Originally posted by Confused but excited.
quote:
Originally posted by nitram38
quote:
Originally posted by Browser
Or just do what Alan Titchmarsh used to do on Ground Force, run some standard flex through a length of garden hose


RCD protected though!


This is not good advice.
You should only use suitably rated flex for low voltage lighting ie; 12 - 24 volts.

[Edited on 29/4/06 by Confused but excited.]


I can see I've got to stop being sarcastic when I reply to posts, or at least post a warning when I am so being
I was kidding for goodness sake! Every time Mr Titsmart and co used to pull this stunt it made me want to shout at the telly. The cable to my shed is SWA buried at least 500mm down with sand and cable run marking tape atop it. One of these light years I'll actually connect the bugger and have mains lights in my two sheds






View User's Profile View All Posts By User U2U Member
Confused but excited.

posted on 2/5/06 at 07:18 PM Reply With Quote
Sorry if I ruffled feathers. This was not my intention.
I too find it annoying when tits on the telly are allowed to pull stunts like that.
It's not like they don't have sparks on set who should know better!
I realise that you were being somewhat tongue in cheek, but someone without any electrical knowlege wouldn't. Hence my reply.
Perhaps I should have worded it more tactfully.
Browser, please accept my unreserved apologies.

[Edited on 2/5/06 by Confused but excited.]

[Edited on 2/5/06 by Confused but excited.]





Tell them about the bent treacle edges!

View User's Profile View All Posts By User U2U Member
Peteff

posted on 2/5/06 at 07:56 PM Reply With Quote
have mains lights in my two sheds

Your name isn't Jackson is it Browser?




Fertang Fertang Biscuit Barrel Two Sheds Jackson





yours, Pete

I went into the RSPCA office the other day. It was so small you could hardly swing a cat in there.

View User's Profile View All Posts By User U2U Member
Jumpy Guy

posted on 2/5/06 at 09:00 PM Reply With Quote
Group hug!!

Now that we're all happy and smiling-

question- can someone confirm that the 12 V DC wiring to the garden lights doesnt need conduit ...

View User's Profile View All Posts By User U2U Member
nitram38

posted on 2/5/06 at 09:57 PM Reply With Quote
12V wiring requires no conduit as there is no shock hazard.
Mechanical protection is another thing.
Building site supplies are 55V to earth, so 12V is well below that level.

[Edited on 2/5/2006 by nitram38]






View User's Profile View All Posts By User U2U Member
Browser

posted on 3/5/06 at 06:58 AM Reply With Quote
quote:
Originally posted by Confused but excited.
Sorry if I ruffled feathers. This was not my intention.
I too find it annoying when tits on the telly are allowed to pull stunts like that.
It's not like they don't have sparks on set who should know better!
I realise that you were being somewhat tongue in cheek, but someone without any electrical knowlege wouldn't. Hence my reply.
Perhaps I should have worded it more tactfully.
Browser, please accept my unreserved apologies.

[Edited on 2/5/06 by Confused but excited.]

[Edited on 2/5/06 by Confused but excited.]


No feathers out of place mate, I was just a bit suprised that's all. Most of the time a smiley at the end of a thread indicates non-serious content
quote:
Originally posted by Peteff
have mains lights in my two sheds

Your name isn't Jackson is it Browser?




Fertang Fertang Biscuit Barrel Two Sheds Jackson


No, my name is not Tarquin Fintimlimbim Fertang Fertang Biscuit Barrel Two Sheds Jackson, it's Kevin Phillips BONGG

I've got two sheds 'cos we live in a single-garage house and I need somewhere to store all of my crap, hence we have an 8'x6' garden shed and a 12'x8' garage store
Oh, and I've got a lean-to down the other side of the house for storing bicycles and timber.

[Edited on 3/5/06 by Browser]

View User's Profile View All Posts By User U2U Member

New Topic New Poll New Reply


go to top






Website design and SEO by Studio Montage

All content © 2001-16 LocostBuilders. Reproduction prohibited
Opinions expressed in public posts are those of the author and do not necessarily represent
the views of other users or any member of the LocostBuilders team.
Running XMB 1.8 Partagium [© 2002 XMB Group] on Apache under CentOS Linux
Founded, built and operated by ChrisW.